r/Fireplaces • u/Right_Wait_9226 • 4d ago
Trouble getting metal flue installed
Installed some handsome Isokerns: two custom see throughs with class A 16” ID, flue by Durachimney (Earthcore didn’t have 16”ID available). Flue runs are 30’ each.
The trouble is getting someone comfortable installing the Duravent product on Isokern. Compounding a bit is that the plans call for a mechanical top mount damper by KW which would be interlocked with the EIS/IPI (gas logs will be installed even though it’s masonry and class A).
Now getting some static that the products aren’t by the same manufacturer (although Isokern engineers already wrote extensive instructions)…
Who should I call on?
6
Upvotes
12
u/Bald_Harry 4d ago
The problem with having products by different manufacturers is that components aren't lab tested with different manufacturers' products. No installer worth their salt will touch that.